  • Industrial automaton engineer here, I’ve worked on a bunch of safety critical systems and audited systems after incidents.

    Best practice in situations were you are sending a remote start command, is for the stop command to be local to the pump controller.

    I audited a system where the main control system sheet a start command to the dosing shed (which stored the concentrated chemicals), unfortunately the stop command was over the same link that got interrupted. The start was received but the stop was never was. Radio is not a reliable link.

    For chemical dosing, I’d expect at least two types of command signals, such as concentration and Max allowed time; you could also measure the weight loss of the concentrate as a third check. Loss of communications to the main controller isn’t necessity an instant stop, but I would expect a prolonged loss to trigger a stop. As long as the local controller has stop control, dosing can usually continue.